artyom@piefed.social 8 hours agoI do know, man.
even if it gets used before getting to the breaker
It would be both added and consumed after the breaker. Like if you had a 10A solar system connected to a dual outlet, and a 10A space heater on the other outlet, there would only be 10A flowing through the outlet, and nowhere else in the system
BT_7274@lemmy.world 8 hours ago
Yes, I was conceding that point. I was then worried about the actual romex in the walls entirely contained after the breaker. Are you able to pump as much power as you want at 15A on a 15A rated wire? There’s got to be some limit, right?
artyom@piefed.social 8 hours ago
No. You can only pump 15A. But you’ll never have more than that.
BT_7274@lemmy.world 8 hours ago
Ok, cool. So if the romex is rated at 15A then I’m going to assume that’s the rated safety limit before things start to get sketchy.
This panel is going to provide 1200w at (I’m assuming) 120v which is 10A.
At that point I plug in something that pulls 1500w (120v for 12.5A total) like a hairdryer.
You’re saying the load on the circuit breaker will be 1500w-1200w for a total of 300w (2.5A), correct? The load on the romex in the walls after the breaker will still be 1500w (12.5A), correct?
What happens if I then plug in a space heater on that same circuit which consumes 1500w (12.5A). The breaker load should then be 15A (the net 2.5A + 12.5A) as it’s rated for and shouldn’t trip, but the load on the romex after the breaker would be 25A (12.5A + 12.5A), 167% its rated capacity.
Am I misunderstanding something? I’m honestly not trying to argue. I’m trying to understand.
artyom@piefed.social 8 hours ago
Yes, that is a problem, but only because you have adjusted the circumstances. I’m not sure how they’re dealing with that.